Bond transformer guard?

Status
Not open for further replies.

sii

Senior Member
Location
Nebraska
I am in the process of installing a 75 kVA transformer in our plant. I will be installing a guard in front of the transformer constructed of 2" x 2" square stel tubing. I couldn't find anything in the NEC but does this guard need to be bonded to ground in any way?
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
Have you considered bonded it simply to the transformer enclosure which should be bonded with an EGC?

I agree with templdl. My inclination is to bond anywhere one can reach between conductive surfaces. So if it is less than 8 feet from the guard to the xfm, I'd bond the two. This is not a code issue, it is a safety design issue.

ice
 