In this case, would we need to isolate the grounded conductor at the meter or at the panel?
I think that 230.82(3) is for 3 phase services. This is single phase.At the service disconnect/panel
A meter disconnect is not a service disconnect and is allowed to be ahead of the service disconnect, this is called "cold sequencing" the meter and can be common with some utility's see 230.82(3) also you use the grounded conductor as the bonding anywhere ahead of the service disconnect as this is.
At the service disconnect/panel
A meter disconnect is not a service disconnect and is allowed to be ahead of the service disconnect, this is called "cold sequencing" the meter and can be common with some utility's see 230.82(3) also you use the grounded conductor as the bonding anywhere ahead of the service disconnect as this is.
I think that 230.82(3) is for 3 phase services. This is single phase.
Just because it is ahead of the meter does not mean it cannot be the service disconnect.
We do a lot of 'cold sequence' metering and the service disconnect and over current protection is ahead of the meter.
However, if you are in an area where the power company takes over control over anything on the supply side of the meter you have to go with a meter disconnect without OCP if you did not do that you would not have access to the over current protection in a service disconnect. (Hope I was clear)
Just because it is ahead of the meter does not mean it cannot be the service disconnect.
We do a lot of 'cold sequence' metering and the service disconnect and over current protection is ahead of the meter.
However, if you are in an area where the power company takes over control over anything on the supply side of the meter you have to go with a meter disconnect without OCP if you did not do that you would not have access to the over current protection in a service disconnect. (Hope I was clear)
Agreed. Many POCO cold sequence rules are that way and you need another service disconnect on the customer side. At first glace it appears that the Milbank product I mentioned earlier can be had with non automatic CB or regular CB to accomodate the application as required.