I already got an answer from the AHJ, but I'm going to post this here because I think its an interesting situation. I'm sure some here have run into this, but this was the first time for me.
Lighting in a commercial warehouse type space is wired at 208V. Where do you pick up power for the exit/emergency lights? While discussing this with the boss, we came up with a couple options.
1) pull a neutral and pick up one leg of the 208V
2) put the exit lights on a 120V circuit by themselves, and install a contactor with a 208V coil
3) put the space lighting on two legs of a 3 pole breaker and the exit lights on the 3rd leg
While nothing is technically wrong with #1, we couldn't find if this was legal or illegal in the code. The problem with 2 or 3, is that the lighting was originally wired all on one circuit so putting the exit/eme lights on a separate circuit is technically against code.