Basement of a non dwelling unit

Status
Not open for further replies.

kwired

Electron manager
Location
NE Nebraska
Only if any conditions mentioned in 210.8(B) are encountered:

(B) Other Than Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in 210.8(B)(1) through (8) shall have ground-fault circuit-interrupter protection for personnel.

(1)
spacer.gif
Bathrooms

(2)
spacer.gif
Kitchens

(3)
spacer.gif
Rooftops


(4)
spacer.gif
Outdoors


Exception No. 1 to (3) and (4): Receptacles that are not readily accessible and are supplied by a branch circuit dedicated to electric snow-melting, deicing, or pipeline and vessel heating equipment shall be permitted to be installed in accordance with 426.28 or 427.22, as applicable.

Exception No. 2 to (4): In industrial establishments only, where the conditions of maintenance and supervision ensure that only qualified personnel are involved, an assured equipment grounding conductor program as specified in 590.6(B)(2) shall be permitted for only those receptacle outlets used to supply equipment that would create a greater hazard if power is interrupted or having a design that is not compatible with GFCI protection.

Electrocution and electrical shock accident data provided by the U.S. Consumer Product Safety Commission indicate that electric shock accidents occur at locations other than dwelling units and construction sites. Although commercial, institutional, and industrial occupancies are not required to have outdoor receptacle outlets installed for general use, there may be outdoor receptacle outlets installed to meet the requirement of 210.63 or at the discretion of the designer or owner. Other than the limited exclusions covered by the two exceptions to 210.8(B)(4), all 125-volt, single-phase, 15- and 20-ampere receptacles installed outdoors at commercial, institutional, and industrial occupancies are required to be provided with ground-fault circuit-interrupter protection.


(5)
spacer.gif
Sinks ? where receptacles are installed within 1.8 m (6 ft) of the outside edge of the sink.



Exception No. 1 to (5): In industrial laboratories, receptacles used to supply equipment where removal of power would introduce a greater hazard shall be permitted to be installed without GFCI protection.

Exception No. 2 to (5): For receptacles located in patient bed locations of general care or critical care areas of health care facilities other than those covered under 210.8(B)(1), GFCI protection shall not be required.

(6)
spacer.gif
Indoor wet locations
(7)
spacer.gif
Locker rooms with associated showering facilities
(8)
spacer.gif
Garages, service bays, and similar areas where electrical diagnostic equipment, electrical hand tools, or portable lighting equipment are to be used
 

Drake5265

Member
Article 210.8 (B)(8)

Article 210.8 (B)(8)

It is is still required in a basement of a non dwelling(8)
spacer.gif
Garages, service bays, and similar areas where electrical diagnostic equipment, electrical hand tools, or portable lighting equipment are to be used
 

Hendrix

Senior Member
Location
New England
It is is still required in a basement of a non dwelling(8)
spacer.gif
Garages, service bays, and similar areas where electrical diagnostic equipment, electrical hand tools, or portable lighting equipment are to be used
That's what I was thinking but, a duplex with a Renai and a condensate pump are what is on the circuit. I'm kind of on the fence on this.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
It is is still required in a basement of a non dwelling(8)
spacer.gif
Garages, service bays, and similar areas where electrical diagnostic equipment, electrical hand tools, or portable lighting equipment are to be used
I beg to disagree. A basement is not a garage. Nor is it a service area. Those terms refer essentially to automobile repair establishments.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Agreed. However, electric hand tools can be plugged into the non GFCI duplex receptacle.
As long as the hand tools are not located in a garage, a service area, or a similar area (which a basement is not), then the GFCI is not needed.
 

kwired

Electron manager
Location
NE Nebraska
As long as the hand tools are not located in a garage, a service area, or a similar area (which a basement is not), then the GFCI is not needed.

I would not say a basement can not be a garage, service area or similar area, although it may not be very common.

Forget the word "basement", it is not in this section and remember the words garage, service area, and other similar areas.
 