exam question...surge arresters

Status
Not open for further replies.

97catintenn

Senior Member
Location
Columbia, TN
How many surge arresters are need for a four wire 3 phase system?

I looked at ART 280.3 Number Required....surge arrester shall be connected to each ungrounded conductor

and I answered 3. Is that correct?
 

Sgriffiths

New member
Location
nj
surge arrestors

surge arrestors

Article 280 surge arrestors, 280.3 in NEC states surge arrestor shall be connected to each ungrounded conductor
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Surge arresters are used on systems over 1kV and I don't think there are 3 phase versions. I think you need one for each phase.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Dennis,
In the real world, that may be a surge arrestor, but in the NEC world that would be a "surge protective device" or "transient voltage surge suppressor" as covered by Article 285.
Surge arrestors are covered by Article 280.
 

guschash

Senior Member
Location
Ohio
I say 3. 285.4 ( the SPD (surge arrestor or TVSS ) shall be connected to each ungrounded conductor. This would be for systems under 1kV.


Article 280.3 surge arrestor shall be connect to each ungrounded conductor,also for systems over 1kV

gus
 
Last edited:

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
If it is a code question and the question uses the term "surge arrestor" it is my opinion you have to look to Article 280 and not 285 for the answer.
 