PurpleHaze
Member
- Location
- Raleigh, NC
I have an installation with a small single phase, single winding transformer that is dedicated to feeding two electric vehicle charging stations. The inspector says that since the chargers are considered continuous loads the transformer is too small because it is not sized at 125% of the full load rating of the chargers. The primary and secondary overcurrent protection is sized at 125% and the primary and secondary conductors are sized for the overcurrent protection. The transformer is UL Listed and rated to carry 100% of its nameplate rating. The transformer rating has not been exceeded by the chargers. I can't find anything in the NEC that supports the inspectors thinking. In fact, it is my understanding that if the breakers were 100% rated, nothing in the circuit would have to be upsized. What am I missing? Any thoughts, comments, similar experiences?