dry type 15kva transformer disconecting means.

Status
Not open for further replies.
Location
OBX, NC.
Im trying to reference the 08 nec for the requirements of disconecting.
The transformer is located 160' from breaker feeding it,, in a separate room.
Do i need a disconect switch... I also need to provide the reference per code to boss man...
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
The reference you want is in the 2011 NEC, article 450.14. That is a new article, and it requires a disconnecting means that is either in sight or lockable. The fact that the article is new in 2011 is what tells you that this is not a requirement for an installation that falls under the 2008.
 

kwired

Electron manager
Location
NE Nebraska
There is no requirement for disconnecting means within sight of a transformer.

450.3 covers overcurrent protection but does not mention location.
 