NEC Aritcle 210.63, if I install a piece of HVAC equipment above a drop-ceiling am I required to install a recepitcle above the drop-ceiling to service the equipment or can my recepticle that is below the drop-ceiling but is within the 25-feet limitation be sufficient if G.F.C.I, protected.
This is in a commercial tenant improvement not a Dwelling, Guest Room or Dormitory. Your response would be helpful. I intrepret this to mean that I just need the recepitcle within 25-feet whether above the ceiling line or below as long as I am on the same level (within the floor, the ceiling would not be considered a different level).
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Art. 210.63 states that the receptacle must be installed on the same level. That could be argued. I would install one in the ceiling.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
IMO the area above a ceiling (unless it's an interstitial space that you can walk on) is not a different level so the receptacle can be anywhere within 25'.
 