Friday I will wire up one of these thankless water heaters.
The 24 Plus Spec sheet has it using 2X50A
Min breaker 2X60, Recommended wire size #6 though the manual reads required #6. The manual also refers to using cable.
* Non-continuous load*
The wire lengths will be less then 10'
I will be using FMC and THHN for this install.
Would not #8 THHN and 50A breakers work for this setup?
I called tech support, no help there.
Thanks