I am running two 120V 20A circuits to a barn. one circuit for lights and one circuit for outlets. #6 AWG THWN is needed for voltage drop. The #6 wires will go into a 8x8x4 junction box before going to the lights and outlets. I would like to decrease the wire size from #6 to #12 to feed the lights and outlets. How many feet are the #12s allowed to be run?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Welcome....
You entitled the thread "taps"..... In case your question addresses the over current protection, take a look at the definition of a tap in 240.2 If you feed the #6s with a 20 amp OCP device, the #12s are not a tap but mere;y an extension of the 20 amp circuit and, as far as overcuurent protection is concerned, there would be not length limitation.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I am running two 120V 20A circuits to a barn. one circuit for lights and one circuit for outlets.
Depending on what code cycle you are working under, you may need to run a 4-wire to a sub-panel in the barn to be code compliant.
The 4 wire I understand, which Code cycle and Artical would require a sub-panel ?
 
Last edited by a moderator:

ner

Member
Location
connecticut
My topic was misleading. Runing #6s to the lights and outlets is impracticle. The distance from the J box where the #6s enter and the lights and outlets (where i want to run #12s) is about 20 feet. I will end up having about 150 feet of #6 with about 20 feet of #12s connected to the end of the #6s. Do I really have to run #6s to the outlets or can I use the #12s for about 20 feet at the end of the run?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If the circuit is protected at 20 amps, you can change over to #12 at any point.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The only way you can run 2 circuits to the separate structure is if they're a MWBC. As Augie stated the #12's will not be tap conductors.
 

kwired

Electron manager
Location
NE Nebraska
Correct me if I'm wrong, but wouldn't you need to hit a 2pole switch that is to be used as a disconnect before hitting the lights and outlets?

That is correct - but it does not need to contain overcurrent protection.

Don't forget your EGC will need to be a #6 also if the conductors are increased to #6. This rules out using a cable assembly with a 10 AWG EGC in it.
 