Looks like you could benefit from a large PV system, but......
1. A quick review of utility incentives for Alabama (see link next line):
http://www.dsireusa.org/incentives/index.cfm?getRE=1?re=undefined&ee=1&spv=0&st=0&srp=1&state=AL
indicates a maximum PV system size of only 50 KW (for incentives) and a Performance-Based Incentive of only $0.12/kWh assuming TVA (only listed Utility).
A drop in the bucket for your situation.
2. For your plant you likely connect to the utility at 12,470V. You can connect at the service voltage or any suitable point at lower voltages. At higher voltages, distance is less of a problem, but you will need an inverter and a suitable transformer, as a start. Needs a full A&E firm to organize. A transmission line is expensive, but possible. When part of a PV system, this can be included in the cost for the Federal investment tax rebates.
3. The utility will have to study the impact of your PV system on their distribution system and may limit the maximum back feed. They may not have much experience with this.
4. Many states have utility rules that allow only a regulated utility to transmit electric power over property lines. A major problem with using nearby land that is not the same parcel. Again, your utility will know the rules that apply. I have several electric service manuals from utilities, but they do not mention this requirement.
For many of the Alabama utilities there seem to be efficiency programs that will help pay for high efficiency lighting retrofits. Also covered by dsireusa.org.