I have a homeowner who wants to put 10lbs of sand into a 5 lb bag. She has a 25kW, 120/240V, 1-Ph generator her contractor has ordered which comes with a factory installed 125/2 main. They want to buy a kit (it's all Generac product) to add a 2nd 125/2.
The system has (2) ATS which have load management (load shed) capability. There are (16) integral "critical" loads within each ATS that are always powered whether we have normal or generator power - unless the generator fails. There are feed thru lugs from each ATS which serve downstream loadcenters at 200A. Now the issue, I know the generator can hold the (16) x 2 = 32 proposed critical circuits. The owner wants to try and hold the rest of the loads in the event of a prolonged outage. She describes just trying to have the ability to move from room to room and have lights which she would shut off. Keep in mind tyhat the house was wired before they dreamed this up so the lighting circuits are already located within loadcenters and cannot be easily pulled to the "critical" circuits at either ATS.
Obviously we would overload this small generator if the entire 320A self contained service was being utilized. At this altitude, the generator can only output ~ 75 Amps. But she is convinced that she can manage the use of laods carefully.
They called me in, I do not usually deal with residential, and I really don't love the thought of this. but I'll be darned if I cannot find a reason to shoot it down other than my opinion that this isn't the way to do it. NEC 702.4(B)(2)(b) says that if load management is utilized, than the source must have the capacity to serve the max load. Now it seems as though because the critical laods are designed to be well below the generator's output capacity, than this isn't disallowed for any reason.
Anyone want to jump in on this?
Thanks
The system has (2) ATS which have load management (load shed) capability. There are (16) integral "critical" loads within each ATS that are always powered whether we have normal or generator power - unless the generator fails. There are feed thru lugs from each ATS which serve downstream loadcenters at 200A. Now the issue, I know the generator can hold the (16) x 2 = 32 proposed critical circuits. The owner wants to try and hold the rest of the loads in the event of a prolonged outage. She describes just trying to have the ability to move from room to room and have lights which she would shut off. Keep in mind tyhat the house was wired before they dreamed this up so the lighting circuits are already located within loadcenters and cannot be easily pulled to the "critical" circuits at either ATS.
Obviously we would overload this small generator if the entire 320A self contained service was being utilized. At this altitude, the generator can only output ~ 75 Amps. But she is convinced that she can manage the use of laods carefully.
They called me in, I do not usually deal with residential, and I really don't love the thought of this. but I'll be darned if I cannot find a reason to shoot it down other than my opinion that this isn't the way to do it. NEC 702.4(B)(2)(b) says that if load management is utilized, than the source must have the capacity to serve the max load. Now it seems as though because the critical laods are designed to be well below the generator's output capacity, than this isn't disallowed for any reason.