jaggedben
Senior Member
- Location
- Northern California
- Occupation
- Solar and Energy Storage Installer
I'm sure this has been discussed ad naseum already, but here goes. This has always confused me.
We installed a solar system on one meter of a building with three meters. The meters are in a single gutter with the panels right above them. The existing GEC was coming from the rod and water, passing through each panel, via nipples between them, and then going from the last panel into the meter enclosure. On the way it was put through bonding bushings on each offset nipple going to the meters.
We wanted to avoid opening the meters, so we crimped our solar to the GEC in the panel, and hoped it would fly, but it did not. The inspector says he can't pass if the system grounding is improper. No real argument with him there.
Here's the thing. He wants the GEC to go to the meters, and then he wants the N-G bonding jumper installed in each panel (the factory supplied jumpers had been left unconnected). So to my mind this creates an N-G bond in both the meters and the panels. Is this okay? Won't there be objectionable current on the bonding jumpers and offset nipples between each panel and the meters? How is this supposed to be done normally?
We installed a solar system on one meter of a building with three meters. The meters are in a single gutter with the panels right above them. The existing GEC was coming from the rod and water, passing through each panel, via nipples between them, and then going from the last panel into the meter enclosure. On the way it was put through bonding bushings on each offset nipple going to the meters.
We wanted to avoid opening the meters, so we crimped our solar to the GEC in the panel, and hoped it would fly, but it did not. The inspector says he can't pass if the system grounding is improper. No real argument with him there.
Here's the thing. He wants the GEC to go to the meters, and then he wants the N-G bonding jumper installed in each panel (the factory supplied jumpers had been left unconnected). So to my mind this creates an N-G bond in both the meters and the panels. Is this okay? Won't there be objectionable current on the bonding jumpers and offset nipples between each panel and the meters? How is this supposed to be done normally?