Good morning. I am trying to determine if an existing circuit will handle the voltage drop for a new increased load. We are replacing a chiller and the existing circuit is 2 parallel runs of 4/0. The new chiller will have a FLA of 381A at 480V, 3-phase and is located 400' away from a new 450A circuit breaker. Using several different voltage drop calculators online, I am getting different values, but somewhere in the neighborhood of 2%. I believe the circuit is fine, but my question is more for my understanding of the voltage drop. I am confused how to apply VD to parallel runs.
Is this the correct equation:
VD = [2(.866)(L=400')(R=0.063 ohm/1000')(I=381A)] / 1000' = 16.63V
% = VD / System Voltage = 16.63 / (480V * Square Root (3)) = 0.0200 = 2.0%
How does the parallel runs play into the equation?