I was wondering if a particular proposed installation would be code compliant.
An 800A breaker from an upstream panel is feeding a set of parallel 3/0 cables. Along the feeder these parallel 3/0 cables are spliced into (4) sets of 3/0 cables which eventually terminate into a 400A main breaker in the downstream panel. I'm not sure of the exact lenghts but am pretty sure both setctions of the feeder cable are greater than 50 ft or so.
I know the (4) sets of 3/0 cables are considered protected by the upstream 800A breaker but was curious if any of the provisions of 240.21 could be applied in order to consider the section of cable with only (2) sets of 3/0 adequately protected?
An 800A breaker from an upstream panel is feeding a set of parallel 3/0 cables. Along the feeder these parallel 3/0 cables are spliced into (4) sets of 3/0 cables which eventually terminate into a 400A main breaker in the downstream panel. I'm not sure of the exact lenghts but am pretty sure both setctions of the feeder cable are greater than 50 ft or so.