I've done a lot of multifamily. I have always been able to use the optional 220.84 multifamily calcs, but those are only allowed when you have elec heat or AC - here I have none. I think I have the right calculation method figured out but would appreciate some feedback.
PART 1, individual unit panel.
For individual dwelling unit panels I can still use the optional 220.82 calcs. They only require a 100A feeder, which will be provided to each unit panel.
220.82(B)(1) Pick largest unit. 725 SF x 3 VA/SF = 2175VA.
220.82(B)(2) 1500VAx2 = 3000VA for kitchen circuits. Central laundry facilities so no third small appliance circuit required.
220.82(B)(3)(a) Add up all appliances: fridge, exhaust fan, microwave/hood (no DW/disposal/etc). 2925VA.
220.82(B)(3)(b) 8000VA range.
220.82(B) 100% of 1st 10kVA plus 40% of remainder: 16100VA -> 10000VA + 0.40 x 6100VA = 12440VA
220.82(C)(1) central heat, no AC. 0 VA.
So....
12440VA / 208V / sqrt(1) = 59.8A. I'll stick with the 100A panel.
PART 2, service panel.
This is where it gets less clear. I can't use 220.84 because of the lack of elec heat or AC in the dwelling units.
1. I figure I take each dwelling unit above (12440VA) and multiply by number of units (twelve) to get that part of the service: 149kVA
2. Then use standard methods for calculating house panel loads (laundry, stairwell and corridor lighting/HVAC/plug loads, exterior lighting, etc). That I have at 57KVA
3. Add them up. 206kVA / 208V / sqrt(3) = 573A.
4. 600A service. Done. (I have metering and distribution worked out with the Owner and Utility, this is just a matter of sizing the service correctly.)
I -think- this is -one- correct way to do it. (Using the "standard" method for individual units would bump me up to an 800A service. House loads would remain the same but each dwelling unit would calc out around 15kVA, times 12 = 180kVA, plus the 57kVA house loads = 237kVA -> ~660A at 208/3.)
Thoughts?
PART 1, individual unit panel.
For individual dwelling unit panels I can still use the optional 220.82 calcs. They only require a 100A feeder, which will be provided to each unit panel.
220.82(B)(1) Pick largest unit. 725 SF x 3 VA/SF = 2175VA.
220.82(B)(2) 1500VAx2 = 3000VA for kitchen circuits. Central laundry facilities so no third small appliance circuit required.
220.82(B)(3)(a) Add up all appliances: fridge, exhaust fan, microwave/hood (no DW/disposal/etc). 2925VA.
220.82(B)(3)(b) 8000VA range.
220.82(B) 100% of 1st 10kVA plus 40% of remainder: 16100VA -> 10000VA + 0.40 x 6100VA = 12440VA
220.82(C)(1) central heat, no AC. 0 VA.
So....
12440VA / 208V / sqrt(1) = 59.8A. I'll stick with the 100A panel.
PART 2, service panel.
This is where it gets less clear. I can't use 220.84 because of the lack of elec heat or AC in the dwelling units.
1. I figure I take each dwelling unit above (12440VA) and multiply by number of units (twelve) to get that part of the service: 149kVA
2. Then use standard methods for calculating house panel loads (laundry, stairwell and corridor lighting/HVAC/plug loads, exterior lighting, etc). That I have at 57KVA
3. Add them up. 206kVA / 208V / sqrt(3) = 573A.
4. 600A service. Done. (I have metering and distribution worked out with the Owner and Utility, this is just a matter of sizing the service correctly.)
I -think- this is -one- correct way to do it. (Using the "standard" method for individual units would bump me up to an 800A service. House loads would remain the same but each dwelling unit would calc out around 15kVA, times 12 = 180kVA, plus the 57kVA house loads = 237kVA -> ~660A at 208/3.)
Thoughts?