nizak

Senior Member
Is there anything in the NEC that states the minimum allowable distance between un insulated fittings(lugs for example) that could be installed in an electrical panel. I'm not asking about bare bus bar for instance,but more so bolt on mechanical lugs used to terminate conductors in a main lug application.Thanks.
 

stevebea

Senior Member
Location
Southeastern PA
Is there anything in the NEC that states the minimum allowable distance between un insulated fittings(lugs for example) that could be installed in an electrical panel. I'm not asking about bare bus bar for instance,but more so bolt on mechanical lugs used to terminate conductors in a main lug application.Thanks.

Table 408.56 speaks of distance speaks of minimum spacing between bare metal parts.
 