300.19 Supporting Conductors in Vertical Raceways.
(A) Spacing Intervals — Maximum. Conductors in vertical raceways shall be supported if the vertical rise exceeds the values in Table 300.19(A). One cable support shall be provided at the top of the vertical raceway or as close to the top as practical. Intermediate supports shall be provided as necessary to limit supported conductor lengths to not greater than those values specified in Table 300.19(A). See related UL
Conductors in long vertical runs must be supported if the vertical rise exceeds the values in Table 300.19(A). This requirement prevents the weight of the conductors from damaging the insulation where they leave the conduit and prevents the conductors from being pulled out of the terminals. Support bushings or cleats such as those shown in Exhibits 300.16 and 300.17 may be used, in addition to many other types of grips manufactured for this purpose.
A vertical raceway contains 1/0 AWG copper conductors. Using Table 300.19(A), if the vertical run is not greater than 100 ft, 300.19(A) requires one cable support near the top of the run. For longer vertical runs, 300.19(A) requires intermediate supports to limit the supported length to the table values. If the vertical run is less than 100 ft, cable supports are not required.
Exhibit 300.16 A support bushing, located at the top of a vertical conduit at a cabinet or pull box, used to prevent the weight of the conductors from damaging insulation or placing strain on termination points.
Exhibit 300.17 Support cleats used to prevent the weight of vertical conductors from damaging insulation or placing strain on termination points.
Exception: Steel wire armor cable shall be supported at the top of the riser with a cable support that clamps the steel wire armor. A safety device shall be permitted at the lower end of the riser to hold the cable in the event there is slippage of the cable in the wire-armored cable support. Additional wedge-type supports shall be permitted to relieve the strain on the equipment terminals caused by expansion of the cable under load.
Changed From 2008
•
Table 300.19(A): Column heading revised for consistency with the terminology used in the section.
(B) Fire-Rated Cables and Conductors. Support methods and spacing intervals for fire-rated cables and conductors shall comply with any restrictions provided in the listing of the electrical circuit protective system used and in no case shall exceed the values in Table 300.19(A). See related UL
Electrical circuit protective systems using fire-rated cable assemblies, generally require more frequent and robust support systems. For example, one manufacturer of Type MI fire-rated cable requires that vertical runs of a two-hour fire-rated assembly be supported every 4 ft, varying substantially from the support requirements of Table 300.19(A).
(C) Support Methods. One of the following methods of support shall be used:
(1)
By clamping devices constructed of or employing insulating wedges inserted in the ends of the raceways. Where clamping of insulation does not adequately support the cable, the conductor also shall be clamped. See related UL
(2)
By inserting boxes at the required intervals in which insulating supports are installed and secured in a satisfactory manner to withstand the weight of the conductors attached thereto, the boxes being provided with covers. See related UL
(3)
In junction boxes, by deflecting the cables not less than 90 degrees and carrying them horizontally to a distance not less than twice the diameter of the cable, the cables being carried on two or more insulating supports and additionally secured thereto by tie wires if desired. Where this method is used, cables shall be supported at intervals not greater than 20 percent of those mentioned in the preceding tabulation. See related UL
(4)
By a method of equal effectiveness.
Ok, I continue to study through the NEC knowing that I am still a novice. I am particularly interested in section A. This part in particular, "One cable support shall be provided at the top of the vertical raceway or as close to the top as practical." The included notes state this, "
A vertical raceway contains 1/0 AWG copper conductors. Using Table 300.19(A), if the vertical run is not greater than 100 ft, 300.19(A) requires one cable support near the top of the run. Are there any exceptions to this or does this mean that ALL panels, pull boxes, etc etc must have the aforementioned supports? Just want to make sure that I am considering everything correctly before I go and start making trouble :angel:
(A) Spacing Intervals — Maximum. Conductors in vertical raceways shall be supported if the vertical rise exceeds the values in Table 300.19(A). One cable support shall be provided at the top of the vertical raceway or as close to the top as practical. Intermediate supports shall be provided as necessary to limit supported conductor lengths to not greater than those values specified in Table 300.19(A). See related UL
Conductors in long vertical runs must be supported if the vertical rise exceeds the values in Table 300.19(A). This requirement prevents the weight of the conductors from damaging the insulation where they leave the conduit and prevents the conductors from being pulled out of the terminals. Support bushings or cleats such as those shown in Exhibits 300.16 and 300.17 may be used, in addition to many other types of grips manufactured for this purpose.
Application Example
A vertical raceway contains 1/0 AWG copper conductors. Using Table 300.19(A), if the vertical run is not greater than 100 ft, 300.19(A) requires one cable support near the top of the run. For longer vertical runs, 300.19(A) requires intermediate supports to limit the supported length to the table values. If the vertical run is less than 100 ft, cable supports are not required.
Exhibit 300.16 A support bushing, located at the top of a vertical conduit at a cabinet or pull box, used to prevent the weight of the conductors from damaging insulation or placing strain on termination points.
Exhibit 300.17 Support cleats used to prevent the weight of vertical conductors from damaging insulation or placing strain on termination points.
Exception: Steel wire armor cable shall be supported at the top of the riser with a cable support that clamps the steel wire armor. A safety device shall be permitted at the lower end of the riser to hold the cable in the event there is slippage of the cable in the wire-armored cable support. Additional wedge-type supports shall be permitted to relieve the strain on the equipment terminals caused by expansion of the cable under load.
Table 300.19(A) Spacings for Conductor Supports |
This table is available as a PDF. Click here to view. |
Changed From 2008
•
(B) Fire-Rated Cables and Conductors. Support methods and spacing intervals for fire-rated cables and conductors shall comply with any restrictions provided in the listing of the electrical circuit protective system used and in no case shall exceed the values in Table 300.19(A). See related UL
Electrical circuit protective systems using fire-rated cable assemblies, generally require more frequent and robust support systems. For example, one manufacturer of Type MI fire-rated cable requires that vertical runs of a two-hour fire-rated assembly be supported every 4 ft, varying substantially from the support requirements of Table 300.19(A).
(C) Support Methods. One of the following methods of support shall be used:
(1)
(2)
(3)
(4)
Ok, I continue to study through the NEC knowing that I am still a novice. I am particularly interested in section A. This part in particular, "One cable support shall be provided at the top of the vertical raceway or as close to the top as practical." The included notes state this, "
Application Example
A vertical raceway contains 1/0 AWG copper conductors. Using Table 300.19(A), if the vertical run is not greater than 100 ft, 300.19(A) requires one cable support near the top of the run. Are there any exceptions to this or does this mean that ALL panels, pull boxes, etc etc must have the aforementioned supports? Just want to make sure that I am considering everything correctly before I go and start making trouble :angel: