Replacing a section of K&T wiring to allow insulation (in California)

Status
Not open for further replies.

brycenesbitt

Senior Member
Location
United States
I've got a wall to insulate, but the inspector is asking for 6' of clearance to the knob and tube wiring. The K&T is in good shape and terminates in a single outlet.The general on the job suggest cutting the K&T back to a junction box, then running romex down the wall. Is this a reasonable approach? And if so, it is reasonable to then find a true earth ground and hook up the equipment ground?----------Note: this is California so Article 394 could apply: California permits insulation over K&T with an inspection certificate. This particular house has 12 gauge K&T. The main house feed is three wires with a shared neutral, protected by a 15 amp double pole AFCI breaker. Kitchen & Laundry are on new circuits.Here's a photo of the current outlet (construction date 1938): DSC_8287.JPG
 

kwired

Electron manager
Location
NE Nebraska
I've got a wall to insulate, but the inspector is asking for 6' of clearance to the knob and tube wiring. The K&T is in good shape and terminates in a single outlet.The general on the job suggest cutting the K&T back to a junction box, then running romex down the wall. Is this a reasonable approach? And if so, it is reasonable to then find a true earth ground and hook up the equipment ground?----------Note: this is California so Article 394 could apply: California permits insulation over K&T with an inspection certificate. This particular house has 12 gauge K&T. The main house feed is three wires with a shared neutral, protected by a 15 amp double pole AFCI breaker. Kitchen & Laundry are on new circuits.Here's a photo of the current outlet (construction date 1938): View attachment 6895

How impractical is it to just run a new branch circuit? After you go through trouble of getting an equipment ground there you may as well have run new circuit in most cases.

Does inspector want 6' or 6 " of clearance?
 

brycenesbitt

Senior Member
Location
United States
6 inches, not 6', that was a typo. And yes of course we could run a totally new circuit... but this one is in rock solid shape. Nice soldered connections, perfect knobs, tubes, unadulterated vintage wiring ready to serve another 75 years.

Can we save it?
 
Last edited by a moderator:

kwired

Electron manager
Location
NE Nebraska
6 inches, not 6', that was a typo. And yes of course we could run a totally new circuit... but this one is in rock solid shape. Nice soldered connections, perfect knobs, tubes, unadulterated vintage wiring ready to serve another 75 years.

Can we save it?

If it is going to be buried in insulation where no one is going to see it, why do you want to? This is not quite the same as being the owner of a Model T in good condition and wanting to show it off
 

brycenesbitt

Senior Member
Location
United States
If it is going to be buried in insulation where no one is going to see it, why do you want to? This is not quite the same as being the owner of a Model T in good condition and wanting to show it off

How about back to the original question: is it code OK to route K&T into a junction box, then complete the stub to an outlet with NM cable?
Does this violate code provisions for "extending" K&T?

Imagine the case where running new wires is too expensive or disruptive to the house or occupants.
 

kwired

Electron manager
Location
NE Nebraska
How about back to the original question: is it code OK to route K&T into a junction box, then complete the stub to an outlet with NM cable?
Does this violate code provisions for "extending" K&T?

Imagine the case where running new wires is too expensive or disruptive to the house or occupants.

That is why there is still a section covering K&T in the code. To enter a box you must enclose the conductor in nonmetallic tubing. I usually run into this problem when trying to re supply a K&T circuit and but not when trying to add additional outlets.

394.10 Uses Permitted. Concealed knob-and-tube wiring shall be permitted to be installed in the hollow spaces of walls and ceilings, or in unfinished attics and roof spaces as provided by 394.23, only as follows:

(1)
spacer.gif
For extensions of existing installations

(2)
spacer.gif
Elsewhere by special permission

You can extend an existing installation. If you add an outlet that does not relieve you of equipment grounding requirements. If you can get an equipment grounding conductor to the added portion - why can't you get a new circuit there?
 

brycenesbitt

Senior Member
Location
United States
You can extend an existing installation. If you add an outlet that does not relieve you of equipment grounding requirements. If you can get an equipment grounding conductor to the added portion - why can't you get a new circuit there?

If I cut the K&T, is it OK to terminate the live K&T wires inside the wall? That's how they'd have done it 'at the time'.
If I'm going to drag the stub ends of the K&T into a box, I might as well use them.
 

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
To insulate over it (in California) most building dept. will want a C-10 licensed electrical contractor to "certify" the K&T as being safe to insulate, in writing. They will make that letter part of the permanent file for that property. Any issue with it in the future and the law suits will be filed against that license holder. So you are now responsible for that 75 year old crap and any future abuse of that circuit.
Sounds like a great idea.
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
The general on the job suggest cutting the K&T back to a junction box, then running romex down the wall. Is this a reasonable approach? . . . .

Here's a photo of the current outlet (construction date 1938):

View attachment 6895
As I am understanding your question, you are suggesting following the K&T conductor coming out of the top of the receptacle outlet back to where it is first exposed by the wall surface removed during your construction project. There you propose to put a junction box and install a new length of NMB back to the receptacle outlet in place of that exposed length of K&T.

And then you propose doing the same thing again to the length of K&T coming out of the bottom of the receptacle outlet.

Two junction boxes.

And you propose to extend a length of the EGC from another branch circuit to connect to the EGC in the new pieces of NMB.

I don't see a problem, by Code, with this. You've shortened the length of old conductor in an existing branch circuit, you haven't added additional outlets, an EGC is added to the existing receptacle outlet, and the insulation envelope is more complete.
 
Last edited:

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
This is an exaple of how to terminate live K&T in the walls/floors. In this case there was a second floor added to an existing house. The roof was taken off and the K&T was not accessible in many places, so the wire was cut and wrapped around the insulaters twice then wrapped around the conductor 4 more times, then cut and insulated.

IMAG0474.jpg IMAG0474.jpg
 

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
Here is a good reason not to leave it for future use.

IMAG0475.jpg

The K&T is feeding the NM, not the other way around.
 