Gfci-type cord cap plugged into gfci protected branch circuit

Status
Not open for further replies.

smallfish

Senior Member
Location
Detroit
Do you see any operational problem in pluging an outdoor spa power cord with a gfci-type cord cap into an outdoor receptacle which is protected in the house service panel by a gfci type breaker?
Thanks
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
In terms of the two GFCI devices being able to do their job or somehow interfering with each other, I see no problem. In terms of what the HO does if the load has a problem and causes a trip, well there may be some confusion about where to go to reset the trip (i.e., if the HO is unaware there are two separate devices).
 