The XLPE cable may not be used at its full current carrying capacity as the cable conductor temperature becomes 90 degree centigrade, whereas the generator terminals, for example, may be rated for 60 degree centigrade only. Only when there are suitable derating factors per site conditions, does the application of XLPE cable become appropriate.XPLE is becoming more common.
Two parallel 185mm2 would do and if there are no abnormal ambients, then possibly even two 150 could handle it.