Ice,
Thanks for the reply. You are correct. I didn't give you the whole facts when I asked you a question. Here is the existing condition and I have to tap this installation for a new work.
The existing 15kV cable comes into the utility tunnel from UG with an m/c armored cable. The armored cable transitioned (spliced) to 15kV CT rated open cables without a j-box after about 500' of run in the tunnel ( I guess they ran out of armored cable??). Can't verify how the gound conductor in the armored cable transitioned to individual open cables.
The support of cable is mixture of cable try, uni-strut support, and cable straps either on the wall or ceiling depend on the locations. Now, is this installation seems to meet NEC?
300.37 lists the available above ground wiring methods.
Guessing the system is 13.8kV Y or 12,460V Y: My biggest concern is the ground/bonding. If there is no ground/bond following along with the single conductors that means any fault current has to be carried by the earth or, the copper tape shields.
If the system is impedance grounded and a ground fault trips within a few seconds, the shields could easily burn up. If the system is solidly ground, a ground fault will vaporize the shields - generally considered not good. I'd be really curious about how the grounding\bonding conductor is continued through the transition from MC to 3 - single conductors.
Now, you say the plan is to T-tap the existing cable using a splice kit? That sounds wrong on so many levels. Lucky for me, you are getting out of my area. Hv&Lv is pretty knowledgable on MV. Maybe he will chime in.
ice