I've got a situation that involves how much loading to allow on a 100 amp main breaker panel.
I'm understanding that max loading on the busbar is limited to 50% of the rating of the panel.
So, the question is can I install a range rated at 50 Amps across from any other circuit breakers in the panel?
This house has been through quite a bit and the previous owner successfully sued kcpl in the past.
The current ower had a near fire due to overloading, but is now up to code and has passed a city inspection and we have managed to put his system back together without any loading over 50 amps per stab.
He is extremely concerned about heat, at this time he is up and running.
That being said, he is wanting to install a 50 Amp range in place of his 30 amp system and we are out of spaces unless I can locate breakers exceeding the 50% limit.
thanks
brian