This code reference uses the term "conditions of use". Is the 125% continuous use factor which is used in 210.19(A)(1) and 215.2(A)(1) considered a "conditions of use" OR is this continuous use factor addressed in 690.8(B)(2)(a)? If the first is true than there will be situations when the 125% continuous use factor is applied alongside the other "conditions of use" factors such as temperature derates and conduit fill derates. If the later is true, than the 125% continuous will not be applied with the other "conditions of use" factors such as temperature derates and conduit fill.
John Wiles from the Institute for Energy and the Environment (IEE) would agree with the later. In his article "Conductor Sizing & Overcurrent Device Ratings" for Home Power Magazine states it this way:
John Wiles from the Institute for Energy and the Environment (IEE) would agree with the later. In his article "Conductor Sizing & Overcurrent Device Ratings" for Home Power Magazine states it this way:
Next is the 125% requirement in 210.19(A)(1) and 215.2(A)(1): "The minimum feeder-circuit conductor size, before the application of any adjustment or correction factor, shall have an allowable ampacity not less than the noncontinuous load plus 125 percent of the continuous load." The emphasized words indicate that there's no requirement to apply the 125% and the condition of use at the same time.
I would appreciate any input on this subject. Thanks.