It DOES affect voltage drop through difference in circuit reactance. See Chapter 9, Table 9, minor columns 2 and 3.... So the choice of conduit would have an impact on the fault calculations (i.e., short circuit and arc flash), but not the voltage drop or load flow calculations.
I believe it is conductor, when you are in SKM - elec. one line diagram, click to any LV cable, link to cable library, then next to cable type column (i.e THHN, THWN) there is another column with text: magnetic or non-magnetic type...
SKM has you choose the conductor, insulation and raceway type all in one library click. It is the raceway that they are asking whether it is magnetic or not.I believe it is conductor, when you are in SKM - elec. one line diagram, click to any LV cable, link to cable library, then next to cable type column (i.e THHN, THWN) there is another column with text: magnetic or non-magnetic type...
SKM is concerned with the type of raceway/conduit being magnetic, non-magnetic or even PVC, the conductor is installed in. Yes the choice is being made in the conductor selection, but that is because of the way the SKM library is created.