Hello.. Need your help regarding fluorescent lamp calculations. Lately, I've encountered problems regarding the load calculations and on the actual current/meter readings. The actual current reading is very high compared to the calculated values. Usually, when I calculate fluorescent loads what I would do is to check the lighting manufacturer ballast catalog, then I use the Input Watts (not the lamp rating). In the catalog, there's also a column for 'mains current during normal operation mA'. Sometimes I noticed that there's a difference in watts calculation if we're to use the current column. Example: for an 18W 220V/60Hz lamp, in the catalog the input power watts is 28, power factor of 0.85. In the 'mains current during operation' the current is 0.352A. If I'm going to use the current, the watts will be different (watts = 0.352A x 220V x 0.85 = 65.8 watts).