Energy. Joules.But there are different classes of SPD's: Some for use at service entrance; some for use at devices inside a home. Their one distinguishing feature is the amount of transient current, they can handle safely
Energy. Joules.But there are different classes of SPD's: Some for use at service entrance; some for use at devices inside a home. Their one distinguishing feature is the amount of transient current, they can handle safely
Carried by current.Energy. Joules.
Volts times amps times seconds.Carried by current.
If there was a fault in the SPD, maybe an MOV that fails short instead of open, how much current can the SPD safely handle without catastrophically failing. That is why a SCR is needed. If there is 200kA available on a SWGR for example, the SPD needs to be rated for 200kA in case that amount of current flows through during a fault in the SPD and we don't want it to blow up, just withstand the fault adequately.
Basic electricity 101. Increase the voltage, same resistance = more current = higher watts. I'm guessing the impedance of the TVSS devices is not linear so change in voltage would not be linear to change in current but it still means if voltage goes up, current goes up. If voltage and current both go up so does the watts.from my research, before picking ditek brand, I found that TVSSs are rated in two areas: 1) max joules capability and 2) max amps. My understanding is if you exceed the max amps, it will blow up or if you exceed the max joules (watt-sec) it can absorb it will blow up. so 2 slightly different limits that both have to be considered in an applications.
They are non-linear devices. Above a specified voltage, they go low impedance thus preventing the voltage from going higher.Basic electricity 101. Increase the voltage, same resistance = more current = higher watts. I'm guessing the impedance of the TVSS devices is not linear so change in voltage would not be linear to change in current but it still means if voltage goes up, current goes up. If voltage and current both go up so does the watts.
They are non-linear devices. Above a specified voltage, they go low impedance thus preventing the voltage from going higher.
It used to be fairly common here to use metal oxide varistors (MOVs) as part of a snubber circuit for protecting semiconductors from overvoltages.
I was never very keen on them myself. That said, we did use Metrosil Silicon Carbide Varistors on a a piece of kit a while back.
It was a static exciter or automatic voltage regulator controlling the field a fairly large alternator. I didn't think it was necessary but the project consultant insisted that it was. To keep a relationship sweet, you sometimes just have to go with the flow.
The overvoltage will be more or less determined at the point where the MOV/TVSS is installed. That's its purpose in life. To prevent damaging voltages getting to equipment.To me that means there is no real way to tell what kind of current will flow in a short circuit, if the amount of voltage is not going to be known, and that is what these devices are about - undetermined high voltage conditions.
It is not called over voltage across the MOV/TVSS, when it is conducting a transient within its rating. It is called clamping voltage.The overvoltage will be more or less determined at the point where the MOV/TVSS is installed. That's its purpose in life. To prevent damaging voltages getting to equipment.
Well, you can call it what you like.It is not called over voltage across the MOV/TVSS, when it is conducting a transient within its rating. It is called clamping voltage.
That's another point. The SPD does not interrupt current. It sinks it.After successfully interrupting the transient current through it, the SPD
After successfully interrupting the transient current through it,
That's another point. The SPD does not interrupt current. It sinks it.
The current ceases when external conditions no longer drive it.
External conditions like the voltage returning to normal after an overvoltage transient.
It isn't a short circuit.I meant by
After successfully interrupting the transient current through it, the SPD
the SPD did not allow the power frequency current to flow through it, thereby making a short circuit.
I agree - it's not a short circuit.Exactly why I am questioning just what this short circuit current rating for these devices is all about.
Amount of current that flows through them is dependent on the voltage of transient and how much power is behind the transient. That is not a short circuit, that is the device doing what it was intended to do.
Again, I agree. Ultimately, failure is because of excessive energy dissipation.If energy level is high enough catastrophic failure should be expected to happen.
I agree - it's not a short circuit.
Again, I agree. Ultimately, failure is because of excessive energy dissipation.
I am sorry but that is a nonsense answer as would be given by a non engineer without a basic understanding of physics.
of course there is a MAX CURRENT rating as well as a MAX POWER rating. Either one can destroy a device.
That infers you can have them independently. You can't (except maybe in the case of a superconductor).I am sorry but that is a nonsense answer as would be given by a non engineer without a basic understanding of physics.
of course there is a MAX CURRENT rating as well as a MAX POWER rating. Either one can destroy a device.