got hit with a violation from a trough to a panel nipple was 26"

as per chapter 9 table 1 #4 max nipple 24" cant find any other reference to max size of nipple.

any thoughts
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
got hit with a violation from a trough to a panel nipple was 26"

as per chapter 9 table 1 #4 max nipple 24" cant find any other reference to max size of nipple.

any thoughts

A nipple is 24" or less and allowed fill is 60% and no derating required. If you are longer than 24" stand fill values and derating applies. Someone else will have to quote the exact code as I don't have a code book handy at the moment.
 

grumpy11

Senior Member
conduit nipple

so at 26" it becomes a short conduit run and all the provisions of conduit fill and derating come into effect.
and of course since its more then 18" it must be supported.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
so at 26" it becomes a short conduit run and all the provisions of conduit fill and derating come into effect.
and of course since its more then 18" it must be supported.

Yes, it becomes a conduit run beyond 24". But in your case, it seems a little petty to me to flag you for this since you are so close. But them's the rules I guess.
 