The residential HVAC world has been taking notes from the rest of the consumer electrical appliance world. In the consumer electrical appliance world, there is a "marketing HP" vs a real HP, and it works like this:
Mechanical HP = Torque (lb.-ft) x RPM / 5250. That is the official definition. Forget that, it means next to nothing to marketing people except as a tool to get them to where they want to go.
Electrical HP = 746W
The "marketing" angle is that when you increase the slip of a motor by loading it, even OVER loading it, you are essentially increasing the HP, even if it is temporary. So let's say you have a motor that is rated for 1.5kW. Electrically, we would call that a 2HP motor (2HP = 1492W). But, if you temporarily overload that motor to the Break Down Torque (BDT) point of 220% of Full Load Torque (FLT), then the mechanical HP formula can be back-fed to say that you have 2.2X the rated torque, thus 2.2X the rated mechanical Power or 3.3kW. Now to be fair, they will also adjust for the fact that the RPM will need to drop to be able to put the motor into BDT, but then they also will say that the PF increases as well, so those issues are a wash (not really, but that's not important to them). So they take that 1.5kW motor and say in their marketing that it develops 4.4HP (3300/746). Now mind you, if the motor stays in BDT for any appreciable length of time, it will overload. It is after all really a 2HP motor. But that's not what they are after, they want you to believe that the motor is larger than it really is.
But if you read the ELECTRICAL rating of Watts or kW, they cannot lie about that because that is what the motor will CONSUME safely at full load according to UL or whoever tested and listed the product. So in essence your guy is sort of right in that if the kW rating changes, the FLA changes, so reading the amps is an indirect way of seeing what is REALLY going on if the nameplate does not show Watts or kW. This has unfortunately become more common, because in other parts of the world, they don't use HP for motors, they use kW. But it's not ELECTRICAL kW, it's MECHANICAL kW, so it can feed right into the hands of these marketing people. That's probably why he said to look at the FLA, because you cannot lie about that.