If all factory neutral lugs are used in an mdp can you install a mechanical lug on the inside of the can if so what article allows that?
If all factory neutral lugs are used in an mdp can you install a mechanical lug on the inside of the can if so what article allows that?
You can, as far as I know, add lugs to the enclosure for equipment grounding conductors.
You can not use the enclosure for grounded conductors {200.2)B)}, or grounding electrode conductors { 250.24(A)(1)}