Reuse of conductors from 3phase circuit to single phase circuit

Status
Not open for further replies.

mshields

Senior Member
Location
Boston, MA
I've got a newly installed 3 phase, 3 wire, 208V homerun for a piece of equipment that, as it turns out, is 120V.

My conductors are therefore color coded Red, Black, Blue and Green. I'd like to avoid having to pull a new 12/2 MC cable by utilizing the Black and with white tape on both ends re-identify either the Blue or the Red as the neutral.

Is this permissible.Would this be a code violation?

Thanks,

Mike
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
200.7 is not a player in this discussion. It speaks of using "whitish" conductors for something other than the neutral.

On the other hand, 200.6(A)(1) would allow marking (e.g,, with white tape) at the terminations for MI cable, but it does not mention MC.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I disagree. 200.7(C) specifically allows this when part of a cable. I think the OP implied MC cable.
(1) If part of a cable assembly and where the insulation is
permanently reidentified to indicate its use as an ungrounded
conductor, by painting or other effective
means at its termination, and at each location where the
conductor is visible and accessible. Identification shall
encircle the insulation and shall be a color other than
white, gray, or green.

It does appear to actually say that.
 

jumper

Senior Member
I've got a newly installed 3 phase, 3 wire, 208V homerun for a piece of equipment that, as it turns out, is 120V.

My conductors are therefore color coded Red, Black, Blue and Green. I'd like to avoid having to pull a new 12/2 MC cable by utilizing the Black and with white tape on both ends re-identify either the Blue or the Red as the neutral.

Is this permissible.Would this be a code violation?

Thanks,

Mike

Code says no, common sense says yes. Want me to do it for ya? I got no qualms doing it.;)
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
200.7 is not a player in this discussion. It speaks of using "whitish" conductors for something other than the neutral.

On the other hand, 200.6(A)(1) would allow marking (e.g,, with white tape) at the terminations for MI cable, but it does not mention MC.

Of course you are right. I was thinking the other way around as you mention. Yes, I think it is not compliant, but is commonly done.
 

mshields

Senior Member
Location
Boston, MA
How about ungrounded conductors

How about ungrounded conductors

Thanks for all the feedback.

Is there a similar rule pertaining to the ungrounded conductors?
 