SG-1
Senior Member
- Location
- Ware Shoals, South Carolina
I am looking at a motor control circuit for a 4160V 4000 HP brushless synchronous motor. The exciter circuit is manual in that the voltage is set with a big knob attached to a variable auto-transformer. The operator has a AC ammeter 0-600A, a DC Voltmeter, a DC ammeter with high/low alarm contacts, & a Power Factor meter to monitor.
The circuit is using a MOC from the feeder breaker to apply the field current, so when the full line voltage is applied the field current is also applied, if the knob is not set back to zero when the motor is stopped. No speed switch or timer is used.
The 55 has an adjustable 0-10 second delay. A SEL 710 is being used for the main motor protection.
Is it very common for an operator to manually adjust the field current from 0 to 10A when starting a sync motor ? I am used to seeing this done with a speed switch or timer.
What would happen if the the excitation is applied at the same moment as the primary voltage ?? Million dollar disaster ?
The circuit is using a MOC from the feeder breaker to apply the field current, so when the full line voltage is applied the field current is also applied, if the knob is not set back to zero when the motor is stopped. No speed switch or timer is used.
The 55 has an adjustable 0-10 second delay. A SEL 710 is being used for the main motor protection.
Is it very common for an operator to manually adjust the field current from 0 to 10A when starting a sync motor ? I am used to seeing this done with a speed switch or timer.
What would happen if the the excitation is applied at the same moment as the primary voltage ?? Million dollar disaster ?