There should be no need for any transformer, just refeed the old service with 208.
If there is a particular piece of equipment that cannot run on 208 I would deal with that separately
I'm curious as to the reason for the change to 208/120V 3? 4W rather than 240/120V 3? 4w? Adding 3? equipment? Or simply needing more power? Was the POCO asked to furnish more compatible voltage, i.e. higher rated 120/240 1? (if no need for 3?), or a 240/120 3? system?New service is 3 phase. Existing is 1 phase. 208 will be the primary.
Hmm... I'm at a loss now. Wind turbines are not on-demand power sources. And if you are going to be grid-tied (necessary to utilize both simultaneously on the same system), you can't tie in turbine supplied 120/208 with POCO furnished 120/240. Is the service getting changed to 208/120 3?, or 120/208 1????The farm is getting a new wind turbine. The turbine puts out 3 phase 480. We step it down to whatever the existing service is. Why the customer changed to 3 phase I don't know as I just started at the company a month ago. The previous electrician did the initial survey 2 years ago and I have to put together the pieces. The plan is to refeed the existing 200 amp service with 208, nothing existing will be severely affected. I was asking the question because of the unbalanced leg issue. The cost of such a transformer is a lot so I'll deal with an unbalanced load.
I am still sketchy about Sketchy's info. Is the new service there or is that what is needed. Each post gets me asking other questions-- could you lay it out more clearly.
Existing service is 120/240 single phase. The new service will be 120/208 3 phase. I plan to re-feed everything with 2 legs of the 208 and neutral.
I understand turbines.The turbine doesn't need a neutral, only the existing farm loads.
In a grid tied system, wouldn't the extra go to the grid, thus balancing the generator outputYour existing neutral could now be loaded effectively equal to a line conductor. This was a big issue in the days of reduced size neutrals.
Will your generator like being so severely unbalanced?
That's why I suggested at least changing out the MDP to 3?... and that's before I knew there was a wind turbine in the picture.Why not try to do a little bit of balancing !-pole circuits across all three phases?
Yes, it would, though I am not sure that the utility is suppling the farm with 3-phase.In a grid tied system, wouldn't the extra go to the grid, thus balancing the generator output.
I understand turbines.
How much of the existing 120/240V infrastructure are you changing?
Sketchy said yes back in post#12...Yes, it would, though I am not sure that the utility is suppling the farm with 3-phase.
Existing service is 120/240 single phase. The new service will be 120/208 3 phase. I plan to re-feed everything with 2 legs of the 208 and neutral.
None. This is my first time doing this and won't be the last. I want to make sure everything works and based on some people I've talked to there won't be an issue re-feeding everything 208. The oven my take a little longer to warm up, motors may run a little slower but there shouldn't be anything severe.