Isolated Ground bar in 400A panel...

Status
Not open for further replies.

Smart $

Esteemed Member
Location
Ohio
I don't know why one would need all 6 back to the panel but if that were the case then sharing a larger conductor would not be any better if one were trying to get a true isolated receptacle. I don't believe a #12 not a #3 would be appropriate for an true isolation
Your last sentence "don't not" make sense. :p
 

kwired

Electron manager
Location
NE Nebraska
Interesting topic.

Let me ask if there is a ground fault in the feeder and if this/these 12 AWG isolated grounding conductors are in same raceway, how much current flows on any of them except for in the case where they may be physically damaged and part of the reason of the fault - like say some ignorant plumber was trying to saw through the feeder raceway with a reciprocating saw. Now say we have a ground fault that happens in the plugged in equipment on the IG circuit. How much current flows in the normal EGC in the feeder?

I'm not trying to choose sides of whether or not the feeder portion of the IG needs sized to the feeder OC device, just asking what type of fault current will the IG be subjected to and what is the real protective device that will stop the fault when opened? With some pretty abnormal conditions being an exception.
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
The isolated ground could have the same fault conditions as a regular EGC, but those would be in the faults from the outlet to the supplied device. That device/appliance/load itself could short, or the cord could fault. So it needs to be sized like a normal EGC.

I don't think the purpose of IG's is to isolate one IG circuit from another, but to keep the EGC isolated from other parallel grounds such as metallic raceways or EGC's of non-isolated circuits. You could think of residential wiring as effectively being IG because of the nonmetallic cable sheaths and boxes.

Every IG install I've seen has an isolated ground bar in the panel supplying the overcurrent devices for the branch circuit. That isolated bar is then either connected to the EGC bar or to its parent upstream bar with a conductor sized per the feeder. If you want to run a bunch of separate insulated ground conductors all the way back to a parent panel, I suppose you could do that and not use a local isolated ground bar, but to me if you put an isolated ground bar in a panel you'd better use a conductor sized per the feeder to serve that bar. If you were installing any circuit (IG or not), would you verify the size of the EGC feeding that isolated bar? I think most are going to assume a ground bar will have been wired with a properly sized conductor. Those bars can get so messy that it is difficult to see which wire is the one feeding it if they are all nearly the same size.

My final argument would be if you had a few individual #12 circuits and you want the IG (common or individual) to go back to an upstream panel with the insulated grounds, you'd be required to use the feeder raceway to keep it "with the circuit conductors". Since the feeder conductors are oversized compared to the #12 circuits, you'd need to upsize the isolated EGC's proportionately as specified in 250.122. A #12 EGC may be too small to allow sufficient fault current if the feeder to the panel is long,
 
Last edited:

kwired

Electron manager
Location
NE Nebraska
The isolated ground could have the same fault conditions as a regular EGC, but those would be in the faults from the outlet to the supplied device. That device/appliance/load itself could short, or the cord could fault. So it needs to be sized like a normal EGC.

I don't think the purpose of IG's is to isolate one IG circuit from another, but to keep the EGC isolated from other parallel grounds such as metallic raceways or EGC's of non-isolated circuits. You could think of residential wiring as effectively being IG because of the nonmetallic cable sheaths and boxes.

Every IG install I've seen has an isolated ground bar in the panel supplying the overcurrent devices for the branch circuit. That isolated bar is then either connected to the EGC bar or to its parent upstream bar with a conductor sized per the feeder. If you want to run a bunch of separate insulated ground conductors all the way back to a parent panel, I suppose you could do that and not use a local isolated ground bar, but to me if you put an isolated ground bar in a panel you'd better use a conductor sized per the feeder to serve that bar. If you were installing any circuit (IG or not), would you verify the size of the EGC feeding that isolated bar? I think most are going to assume a ground bar will have been wired with a properly sized conductor. Those bars can get so messy that it is difficult to see which wire is the one feeding it if they are all nearly the same size.

My final argument would be if you had a few individual #12 circuits and you want the IG (common or individual) to go back to an upstream panel with the insulated grounds, you'd be required to use the feeder raceway to keep it "with the circuit conductors". Since the feeder conductors are oversized compared to the #12 circuits, you'd need to upsize the isolated EGC's proportionately as specified in 250.122. A #12 EGC may be too small to allow sufficient fault current if the feeder to the panel is long,
I like that last part as a good argument for increasing the size that is run with the feeder. Kind of no different than if the feeder were just oversized branch circuit conductors because of voltage drop reasons.
 

Eng

Member
Just curious, what load do these IG recptacles serve ? Do these IG recptacles provide any

added benifit or protection ? Elimination of noise ? Eng, hang out here long enough &

you will get a feeling for the general disdain of IG recptacles.

This is a requirement of our client (State of Minnesota). We are required to provide IG receptacles next to each voice/data connection.
 