I am getting a 10KW system installed for a relative.<br>
They have a 200AMP load center.<br>
Per NEC code it needs to be downsized to 175A main breaker.
Unfortunately, she has a Siemens PL series 200A load center and Siemens does NOT make a 175A Main Breaker Kit. So instead of just swaping out the main breaker.... we need to do the following:
1. Take out exsisting Siemens 200A Breaker and replace it with two main lugs.<br>
2. Install a new panel with a 175a main Breaker in it
; which feeds the exsisting Siemens panel.
I've gone to a few electrical supply places and NONE of them have heard of a 175 main breaker kit. I finally just ordered a GE one online. It was not easy to find, but I'm resourceful.
Next hurdle was finding an Enclosure/panel, Only ones I could find were full sized 200AMP whole house load centers. It is impractical to put another full size panel in the garage
So I took a smallish 125A breaker box and gutted it.
Put 1/4" thick piece of plastic on the bottom and then bolted the 175A breaker on top
Put Three Main lugs into the panel. One for ground, black and Red.
There was no real way to attach them so I took a 1/4-20 bolt and bolted them on.
Will this pass code? Would you make any changes?
See photo below
http://s9.postimage.org/gxfzxwy19/electrical_panel.jpg
They have a 200AMP load center.<br>
Per NEC code it needs to be downsized to 175A main breaker.
Unfortunately, she has a Siemens PL series 200A load center and Siemens does NOT make a 175A Main Breaker Kit. So instead of just swaping out the main breaker.... we need to do the following:
1. Take out exsisting Siemens 200A Breaker and replace it with two main lugs.<br>
2. Install a new panel with a 175a main Breaker in it
; which feeds the exsisting Siemens panel.
I've gone to a few electrical supply places and NONE of them have heard of a 175 main breaker kit. I finally just ordered a GE one online. It was not easy to find, but I'm resourceful.
Next hurdle was finding an Enclosure/panel, Only ones I could find were full sized 200AMP whole house load centers. It is impractical to put another full size panel in the garage
So I took a smallish 125A breaker box and gutted it.
Put 1/4" thick piece of plastic on the bottom and then bolted the 175A breaker on top
Put Three Main lugs into the panel. One for ground, black and Red.
There was no real way to attach them so I took a 1/4-20 bolt and bolted them on.
Will this pass code? Would you make any changes?
See photo below
http://s9.postimage.org/gxfzxwy19/electrical_panel.jpg