mkgrady
Senior Member
- Location
- Massachusetts
What code cycle made expansion couplings a requirement?
I have to resolve a problem where a condo complex was built around 1982. There are 24 buildings with meter centers containing 4-6 meters. All service laterals are in 4" PVC and each unit is fed underground in 1 1/2" PVC. Some of the conduits have pulled out of the male adapters and some conduits are pushing up on the enclosure making the enclosure cock eyed.
The reason I was called by the owners is because a GC was hired to put new siding on a six of the buildings. When he disconnected one of the meter center from the wall it blew up. The fasteners were external so he may not have opened the enclosure to unscrew it from the wall. He did not have the same problem at the other five buildings but he should have had an electrician work on the meter center not a carpenter. It may be that the original installation has screws through the back of the enclosure in addition to the external ones and when they pried it off the wall a screw fell in and shorted the bus.
I have been asked to evaluate the condition of the 18 other buildings, to make recomendations for any fixes, and to tell the owner if the GC is responsible for the cost of the repairs. I am told the GC invoiced the condo for $10K to replace the meter center and to go to five of the other buildings he has re-sided to clamp the PVC conduits to the wall under the meter center.
My first impressions are that an electrician would have recognized if a meter center was cockeyed (nobody knows if it was) it may be a disaster waiting to happen and it would not have been moved without a thorough inspectuion for internal problems, and that going to the other five buildings to clamp the conduits to the wall is a way for the GC to save face and get paid for the extra work
I have to resolve a problem where a condo complex was built around 1982. There are 24 buildings with meter centers containing 4-6 meters. All service laterals are in 4" PVC and each unit is fed underground in 1 1/2" PVC. Some of the conduits have pulled out of the male adapters and some conduits are pushing up on the enclosure making the enclosure cock eyed.
The reason I was called by the owners is because a GC was hired to put new siding on a six of the buildings. When he disconnected one of the meter center from the wall it blew up. The fasteners were external so he may not have opened the enclosure to unscrew it from the wall. He did not have the same problem at the other five buildings but he should have had an electrician work on the meter center not a carpenter. It may be that the original installation has screws through the back of the enclosure in addition to the external ones and when they pried it off the wall a screw fell in and shorted the bus.
I have been asked to evaluate the condition of the 18 other buildings, to make recomendations for any fixes, and to tell the owner if the GC is responsible for the cost of the repairs. I am told the GC invoiced the condo for $10K to replace the meter center and to go to five of the other buildings he has re-sided to clamp the PVC conduits to the wall under the meter center.
My first impressions are that an electrician would have recognized if a meter center was cockeyed (nobody knows if it was) it may be a disaster waiting to happen and it would not have been moved without a thorough inspectuion for internal problems, and that going to the other five buildings to clamp the conduits to the wall is a way for the GC to save face and get paid for the extra work