I was wondering which has more flexibility, ENT or non metallic liquid tight. I have a rather tight offset I need to make in a pvc run. Thanks in advance.
The minimum permitted bend radius is the same for both products. The .24 sections of Articles 356 and 362 both refer you to Chapter 9, Table 2 for the minimum permitted bend radius.I was wondering which has more flexibility, ENT or non metallic liquid tight. I have a rather tight offset I need to make in a pvc run. Thanks in advance.
The minimum permitted bend radius is the same for both products. The .24 sections of Articles 356 and 362 both refer you to Chapter 9, Table 2 for the minimum permitted bend radius.
Doh, I didn't catch that Don. Gerry, what did you end up doing since you couldn't make that offset happen? This is 1 1/4" I'm working with.
ENT has the advantage that it can be used directly with the PVC fittings. To place a portion of ENT in a PVC run you just use the PVC couplings (or the bell ends found on PVC) and glue theENT into them. The corrugated interior of the ENT can make pulling harder, especially through bends (harder than through PVC). The minimum radius of ENT bends is the same as PVC bends.
my experience with ENT is that it pulls easier, and is easier to blow string thru.
it'll bend in a tighter radius without flattening than anything else. you are still
constrained by the minimum bending radius in the code for the conduit size
you are using.... but it'll bend a LOT tighter than that.... :angel:
last week, i put 10' of 2" smurf in a mantle for the flat screen over the fireplace,
and it had a shwoop and a ninety, while fitting thru the bulkheads in the mantle.
it was for AV cables, and the shwoop was probably a 4" radius. i notched the 3x4
flyer above the fireplace, got the thing with 3' sticking out of the mantle for some
leverage, and bent it double while 4 folks put the mantle up.... (large mantle)
got it in place, sliced it flush with the drywall, and put a couple large head screws
thru it to hold it in place, and patched the drywall.
it's almost impossible to kink it.
I hope that you will be able to pull through such a tight bend. In a perfect world I prefer rigid conduit 90's or long sweeping bends of PVC, obviously.
Seen too many ropes/strings cut through the inside of a bend making it impossible to pull through.
Please let me know how it works out for ya.
I hope that you will be able to pull through such a tight bend. In a perfect world I prefer rigid conduit 90's or long sweeping bends of PVC, obviously.
Seen too many ropes/strings cut through the inside of a bend making it impossible to pull through.
Please let me know how it works out for ya.
lotta folks use GRC 90's for exactly that reason...
i'm a huge fan of muletape.... it doesn't cut thru plastic at all....
and muletape is cheaper than 3 or 4 two inch grc 90's.....