Number of wires includes ground?

Status
Not open for further replies.

cppoly

Senior Member
Location
New York
Basic question here, does the number of wires listed in a product data sheet include ground?

A datasheet says the electric requirement is 220V - 3 wire but doesn't specify single or 3 phase. Single phase could be 2 hots + 1 ground to satisfy 3 wire. Or 3 phase could be 3 hots to satisfy 3 wire if the ground isn't included. Does the NEC have a standard on this?

Also, this equipment is for commercial buildings, so shouldn't the voltage be really specified at 208V? It's a violation to provide the wrong voltage for equipment. B/c after voltage drop the equipment might only see 200 V...
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
In general, the EGC is not counted when you see a spec like that.

A grounded conductor would be counted, so that spec could be for a three phase system with three ungrounded conductors, or for a single phase system with two ungrounded conductors and a grounded conductor.
 

realolman

Senior Member
Basic question here, does the number of wires listed in a product data sheet include ground?

A datasheet says the electric requirement is 220V - 3 wire but doesn't specify single or 3 phase. Single phase could be 2 hots + 1 ground to satisfy 3 wire. Or 3 phase could be 3 hots to satisfy 3 wire if the ground isn't included. Does the NEC have a standard on this?

Also, this equipment is for commercial buildings, so shouldn't the voltage be really specified at 208V? It's a violation to provide the wrong voltage for equipment. B/c after voltage drop the equipment might only see 200 V...

That's a pretty crappy non-specific spec IMO... why would anybody even write a thing like that?
 

Smart $

Esteemed Member
Location
Ohio
...

Also, this equipment is for commercial buildings, so shouldn't the voltage be really specified at 208V? It's a violation to provide the wrong voltage for equipment. B/c after voltage drop the equipment might only see 200 V...
Some manufacturers choose to indicate equipment that will operate on either 240V or 208V systems as 220V, as it is within +/-10% of both.
 