Status
Not open for further replies.

rookie4now

Senior Member
There are 4 9Kw HVAC units (36Kw total). The service is 120/240 3P. I thought the current would be (I=36,000/(240*1.73)) which comes to 86.7 amps per leg. When I plug it in to the load calculator, it comes up with 50 amps. While I'm on the topic, what are the total available Kw on a 300a 120/240 service?

thanks
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If it's 50 amps, we are both overlooking something.

In a balanced situation the 300 amp service would be rated 124.5 kw (not taking continuous vs non-continuous into account)
 