That's fine but it might not fit into the 100 amp terminals. Also you may need to increase the size of your GEC's
What is the purpose of this. It does not increase the service size.My thinking was that I'd use 100a cable from meter to panel
What is the purpose of this. It does not increase the service size.
My thinking was that I'd use 100a cable from meter to panel
The service cable is frayed so needs to be replaced but panel is fine. Customer is trying to keep cost down for now but allow increase to 200a in future.
That would work if the 200 amp meter enclosure had lugs small enough for the 100 amp coductors. Also the GEC woud need to be sized according to the largest service entrance conductors which in this case would be the 200 amp conductors.
(2) Individual Grounding Electrode Conductors. A
grounding electrode conductor shall be connected between
the grounded conductor in each service equipment disconnecting
means enclosure and the grounding electrode system.
Each grounding electrode conductor shall be sized in
accordance with 250.66 based on the service-entrance conductor(
s) supplying the individual service disconnecting
means.
GEC sized to 100 Amps
(2) Individual Grounding Electrode Conductors. A
grounding electrode conductor shall be connected between
the grounded conductor in each service equipment disconnecting
means enclosure and the grounding electrode system.
Each grounding electrode conductor shall be sized in
accordance with 250.66 based on the service-entrance conductor(
s) supplying the individual service disconnecting
means.
GEC sized to 100 Amps
It's my opinion... you can't have it.IMO, the size would depend on where the connection was made. If you connected the GEC at the meter, I would say you would size it per the service conductors supplying the meter. If you connected at the service disconnect means, I would say size per the service conductors supplying the disconnect.
Again, my opinion.
IMO, the size would depend on where the connection was made. If you connected the GEC at the meter, I would say you would size it per the service conductors supplying the meter. If you connected at the service disconnect means, I would say size per the service conductors supplying the disconnect.
Again, my opinion.
That doesn't apply here because you left out the heading of that section "(D) Service with Multiple Disconnecting Means Enclosures."
Take a look under the heading of Table 250.66. It says "Size of Largest Ungrounded Service-Entrance Conductor or Equivalent Area for Parallel
Conductors (AWG/kcmil)"
Correct wrong section:
250.66 Size of Alternating-Current Grounding Electrode
Conductor. The size of the grounding electrode conductor
at the service, at each building or structure where
supplied by a feeder(s) or branch circuit(s), or at a separately
derived system of a grounded or ungrounded ac system
shall not be less than given in Table 250.66, except as
permitted in 250.66(A) through (C).
This single service has two different sized SEC's you need to size the GEC according to the largest.
IMO, the size would depend on where the connection was made. If you connected the GEC at the meter, I would say you would size it per the service conductors supplying the meter. If you connected at the service disconnect means, I would say size per the service conductors supplying the disconnect.
Again, my opinion.
As stated previously the SEC's begin at the drop. How is using the smaller SEC's permitted where T250.66 says to use the largest?
That would work if the 200 amp meter enclosure had lugs small enough for the 100 amp coductors.
That's a good point that I hadn't thought of. Does anyone know the wire size range for the lugs in a 200a meter?
That would work if the 200 amp meter enclosure had lugs small enough for the 100 amp coductors.
That's a good point that I hadn't thought of. Does anyone know the wire size range for the lugs in a 200a meter?
http://www.milbankmfg.com/Products/Catalogs/CatalogFiles/PDF/REC.pdf
Your interpretation of "largest" is one of at least two possible interpretations:As stated previously the SEC's begin at the drop. How is using the smaller SEC's permitted where T250.66 says to use the largest?