Hm, my understanding of voltage/power/current is that a 5 kw heater is going to draw the amps required for 5 kw regardless of the voltage. That is, it would draw 20.83A if wired at 240V and 24.04A if wired at 208.
If you have a 240V rated water heater and power it with a 208V system, it's going to run at 208V. I don't see how getting a 240V heater is going to help anything in this situation.
If the load is inductive like a motor the power will remain fairly constant, if voltage goes up, current goes down, if voltage goes down current goes up. There will be limitations but to go from 208 to 240 will result in similar net power.
For resistive loads (water heater most likely is unless it is a heat pump) the resistance remains constant no matter what voltage is applied. If it is rated @ 208 volts and you apply 240 instead the resistance still remains the same and an increase in voltage will result in an increase in current.