dicklaxt

Senior Member
True but thats an unintentional path,not much you can do about that and that would still exist without the intentional path made by bonding.I guess maybe its averting a potentional shock hazard with ne of the internal splices somehow going to ground.

dick
 

jap

Senior Member
Occupation
Electrician
That meaning the only way I think that would be less hazardous would be if you had a weak link in the conduit system back to the panel which would interfere with the fault return path.

In that case the ground wire that you just bonded to the junction box would carry the fault back instead of the conduit.

Like I stated before. Thats why I think of the equipment grounding conductor as a reinforcement of the conduit return path, not so much as a parallel return path.