WCULPEPPER
- Meridian,MS,USA
What isn the minimum distance from the service head to the point of attachment?
I don't recall every seeing a minimum distance in the NEC. In fact , I don't think there is a maximum distance either. The point of attachment is mounted to the service mast when a mast is installed so it is generally directly under the head.What isn the minimum distance from the service head to the point of attachment?
Sorry there is a max- 24"
That is correct Dennis. In addition the service head in 99.99999 % of the time is to be located above the point of attachment (230.54(C) unless you get special dispensation from the AHJ and/or the POCO.Point of attachment is the actual point where the service drop conductors attach to the building/pole, etc
Why would it be different for conduit? The issue is water traving down the space between the strands under the conductor insulation. This is a problem for both cable and conduit installations any time the splice to the service drop is made above the service head.Even for conduit?
Just typical poor code wording.IMO his referenced code section {230.54(C)} does not address conduit, only SE cable.
Seems logical doesn't it ?although they would have the same issue as SE cable with the POA located above the weatherhead.