I had a debate with other engineer on how to size the panelboard on the secondary side of the 75KVA transformer.
We have a 75KVA (480V to 120/208V) transformer to feed a 120/208V. Our load at the panel will be less than 140A. He insists that he needs a 400A panel with 300A main to meet the code. Here is what he did.
FLA of secondary is 208A. Secondary OCPD is 208x1.25=260A. Next size up is 300A (per 450.3). His secondary conductor will be 350KCM per 240/21(c).
I would say that is totally a waste of money and that is not the code requirement.
What I would do is, first calculate the load and decide what size transformer I would need. With 140A load, I would need a 75 kVA transformer (140x208x1.732=50.4kVA). For a secondary panelboard, I would provide a 225A panelboard with 225A main since my load is only 140A and the FLA of 75kVA transformer is only 208A. My transformer conductor will be #4/0. I think this is perfectly in compliance with the code.
What would you guys normally size the secondary panelboard for 75kVA transformer?
We have a 75KVA (480V to 120/208V) transformer to feed a 120/208V. Our load at the panel will be less than 140A. He insists that he needs a 400A panel with 300A main to meet the code. Here is what he did.
FLA of secondary is 208A. Secondary OCPD is 208x1.25=260A. Next size up is 300A (per 450.3). His secondary conductor will be 350KCM per 240/21(c).
I would say that is totally a waste of money and that is not the code requirement.
What I would do is, first calculate the load and decide what size transformer I would need. With 140A load, I would need a 75 kVA transformer (140x208x1.732=50.4kVA). For a secondary panelboard, I would provide a 225A panelboard with 225A main since my load is only 140A and the FLA of 75kVA transformer is only 208A. My transformer conductor will be #4/0. I think this is perfectly in compliance with the code.
What would you guys normally size the secondary panelboard for 75kVA transformer?