mkgrady
Senior Member
- Location
- Massachusetts
I need to wire three 2 HP motors with one circuit available to serve them. The motors and circuit are three phase 480 volts. The circuit is #12 wire on a 20 amp breaker. FLA of each motor is 2.7 so the circuit appears to be large enough. The motors will not be run continuous. These motors will be protected against overload by way of the starter heaters. Will the starters also protect against short circuit and ground fault? Or do I need to use fused disconnects at the motors and fuse them at 250% of FLA for each motor? How do I fuse at 6.75 amps? NEC 430 has so much in it. I could use some help with this. Thanks