I have a AC/DC Arc Welder. The nameplate amps are 40A @ 240V Single phase with a 60% Duty cycle.
40a x 60% Multiplier of .78 = 31.2 A = #10 thhn conductor.
Conductor #10
OCPD 80A ( 40A x 200 % = 80A)
An if I use a Disconnect what size would I need.
I will have a Breaker in panel an disconnect an receptacle at the welder location
 

wmeek

Senior Member
Location
Texas
Occupation
Electrician
It appears that I will need a 80A OCPD, #8 THHN Conductors an a 100A Non Fused disconnect
 