121031-0930 EDT
My neighborhood has a 3 phase delta supply.
The night before last my neighbor's, different transformer and phase, lost power about midnight. I did not loose power, and I do not know what my voltage was. My voltage could have been low, meaning 90 to 100 V.
Just after 7 AM yesterday my lights flickered some. Then out my back window I noticed arcing near the ground along the pole line and about 1 to 2 houses away in a tree-ed area. Some while later the fire department came and put up yellow tape.
I looked at my voltage and it was jumping around, and therefore I decided about 9 AM to set up my generator. It is a Honda 5000 W.
Went next door to the new neighbors, different than the above mentioned neighbor, and turned off their main breaker. They have a very large side-by-side freezer-refrigerator. I told them I could power the refrigerator. Ran an extension cord to them. Checked the power input and it was almost 900 W. Quite large. Voltage was 110 V at their end of my 120 foot extension cord. About 118 V at the generator. For comparison my large freezers are about 300 W initially and drop to about 180 W.
When I first powered my generator I could not connect the house load because the generator stalled. This results from 4 motors all wanting to start at the same time, plus other loads.
Remove loads, got generator running, then gradually added loads. Normal daytime house load is 2 to 3 kW. Once the system is up and running there is no problem because the likelihood of more than one motor starting at the same time is near zero.
I should have used less than than 30 kWh on the generator yesterday and fuel consumption was about about 6 gallons of gasoline. Gasoline is worth about 33 kWh per gallon. Thus, overall efficiency was less than 16%. An important question is how to greatly increase this efficiency?
Because the generator is too noisy to run all night it was shut down about 11:30 PM. In preparation for this I bought 14 # of dry ice. Normal internal freezer temperature is about 0 F. 5# of dry ice was put in each large freezer at about 8 PM. Washtenaw Dairy closed at 9 PM so I could not wait until later to get the dry ice. 4 # was put in the freezer part of the refrigerator-freezer. My neighbor had no idea how much dry ice to use for her freezer and she bought #15. By 11:30 PM most of my 5# block was gone. So her 15 # was a better estimate of a needed value for overnight.
My big freezer temperature was up to 20 F at 7:00 AM today. In the ref-freezer combination the freezer temperature was up to 27 F.
Outside temperature was about 40 F overnight. House temperature was 70 F at 11:30 PM and 65 F at 7 AM. Wind was not too great last night. Under these conditions the thermal time constant of the house is about:
(70-65)/(0.63*30) = 0.26 for the portion of one time constant.
The time for this change is 7.5 hours.
Thus, approximate thermal time constant is 7.5/0.26 = 28.8 hours.
The electrical problem is one lost phase on the primary distribution lines.
The downed wire and arcing were located beyond my transformer. So until DTE opened the phase, probably at the substation, I still had power but some flickering. I had no usable power after my phase was opened somewhere between the substation and before my transformer. I have monitored my source voltage at various times thru the last day and it has varied from 20 V to 104 V based on 120 V. Thus, many neighbors have loads that are cycling on and off (thermal overloads kicking off) that have not opened their main breaker. This is much like the problem of an open neutral. Houses that share the open phase provide a split load across the one functional phase. As the load impedances change on each side of the open phase it changes the voltage distribution.
Dry ice is about $1.25 per pound in small quantities. 15 # is probably a reasonable minimum for a large freezer for 8 to 10 hours. The generator approach is less expensive than the dry ice approach.
.
My neighborhood has a 3 phase delta supply.
The night before last my neighbor's, different transformer and phase, lost power about midnight. I did not loose power, and I do not know what my voltage was. My voltage could have been low, meaning 90 to 100 V.
Just after 7 AM yesterday my lights flickered some. Then out my back window I noticed arcing near the ground along the pole line and about 1 to 2 houses away in a tree-ed area. Some while later the fire department came and put up yellow tape.
I looked at my voltage and it was jumping around, and therefore I decided about 9 AM to set up my generator. It is a Honda 5000 W.
Went next door to the new neighbors, different than the above mentioned neighbor, and turned off their main breaker. They have a very large side-by-side freezer-refrigerator. I told them I could power the refrigerator. Ran an extension cord to them. Checked the power input and it was almost 900 W. Quite large. Voltage was 110 V at their end of my 120 foot extension cord. About 118 V at the generator. For comparison my large freezers are about 300 W initially and drop to about 180 W.
When I first powered my generator I could not connect the house load because the generator stalled. This results from 4 motors all wanting to start at the same time, plus other loads.
Remove loads, got generator running, then gradually added loads. Normal daytime house load is 2 to 3 kW. Once the system is up and running there is no problem because the likelihood of more than one motor starting at the same time is near zero.
I should have used less than than 30 kWh on the generator yesterday and fuel consumption was about about 6 gallons of gasoline. Gasoline is worth about 33 kWh per gallon. Thus, overall efficiency was less than 16%. An important question is how to greatly increase this efficiency?
Because the generator is too noisy to run all night it was shut down about 11:30 PM. In preparation for this I bought 14 # of dry ice. Normal internal freezer temperature is about 0 F. 5# of dry ice was put in each large freezer at about 8 PM. Washtenaw Dairy closed at 9 PM so I could not wait until later to get the dry ice. 4 # was put in the freezer part of the refrigerator-freezer. My neighbor had no idea how much dry ice to use for her freezer and she bought #15. By 11:30 PM most of my 5# block was gone. So her 15 # was a better estimate of a needed value for overnight.
My big freezer temperature was up to 20 F at 7:00 AM today. In the ref-freezer combination the freezer temperature was up to 27 F.
Outside temperature was about 40 F overnight. House temperature was 70 F at 11:30 PM and 65 F at 7 AM. Wind was not too great last night. Under these conditions the thermal time constant of the house is about:
(70-65)/(0.63*30) = 0.26 for the portion of one time constant.
The time for this change is 7.5 hours.
Thus, approximate thermal time constant is 7.5/0.26 = 28.8 hours.
The electrical problem is one lost phase on the primary distribution lines.
The downed wire and arcing were located beyond my transformer. So until DTE opened the phase, probably at the substation, I still had power but some flickering. I had no usable power after my phase was opened somewhere between the substation and before my transformer. I have monitored my source voltage at various times thru the last day and it has varied from 20 V to 104 V based on 120 V. Thus, many neighbors have loads that are cycling on and off (thermal overloads kicking off) that have not opened their main breaker. This is much like the problem of an open neutral. Houses that share the open phase provide a split load across the one functional phase. As the load impedances change on each side of the open phase it changes the voltage distribution.
Dry ice is about $1.25 per pound in small quantities. 15 # is probably a reasonable minimum for a large freezer for 8 to 10 hours. The generator approach is less expensive than the dry ice approach.
.