Proposal 2-134 and branch circuit neutral size 210.19

Status
Not open for further replies.

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
proposal 2-134 said:
Recommendation: Add new text to read as follows:
210.19(A)(5) Grounded Conductor. The size of the branch circuit grounded
conductor shall not be smaller than that required by 250.122, except that
250.122(F) shall not apply where grounded conductors are run in parallel.
Substantiation: As the code is now, it is possible, although a rare occurrence,
where one could reduce a branch circuits grounded conductor?s size smaller
than the ungrounded conductors and the equipment grounding conductor, but
under 210.19(A)(4) it is possible. In 215.2(A)(2) for feeders we have guidance
that the grounded conductor must not be smaller than the EGC that is required
in Table 250.122. We are not given that same assurance for a branch circuit. I
believe it is never the intent of the NEC to allow a grounded conductor to be
smaller than the required equipment grounding conductor.
Panel Meeting Action: Reject
Panel Statement: It is unclear to the panel how the submitter is interpreting
that 210.19(A)(4) could result in a grounded conductor smaller than the
ungrounded conductors and the equipment grounding conductor.
Number Eligible to Vote: 11
Ballot Results: Affirmative: 11
________________________________________________________________

Here was a interesting proposal dealing with L-N faults, any set of wires in a circuit should be capable of tripping the OCPD. If for some reason the ECG is increased in size beyond the size in 250.122 the neutral (read grounded conductor) can be smaller than the ECG but not smaller than 250.122. Seems fine with since conduit could be the EGG or the ECG could be upsized for sharing with a larger circuit. OK Looks like a good proposal.

Now I am not getting the reasoniong why the panel rejected it?
210.19(A)(4) permits conductors to be sized at an ampacity sufficient for the loads served.
Seems like neutrals need to be sized for the neutral load.
Where in the NEC are multi wire branch circuit conductors required to all be the same size for say a hot tub?
Did the panel not consider a standard 11kw hot tub with #6cu THHN, ECG of 8 THHN (oversized) and a 14 AWG neutral. It has a 750W neutral load for a light and blower, what is preventing someone from pulling a 14awg neutral?
Thanks

The proposal could have removed the 210.19 (3) exception #2 that requires a 10AWG neutral on a 2.5 kw 3 wire 20A counter top cooker circuit as well.
 

jumper

Senior Member
The proposal could have removed the 210.19 (3) exception #2 that requires a 10AWG neutral on a 2.5 kw 3 wire 20A counter top cooker circuit as well.

I believe that section is for equipment of 8 3/4kW and above.

Exception No. 2: The neutral conductor of a 3-wire
branch circuit supplying a household electric range, a
wall-mounted oven, or a counter-mounted cooking unit
shall be permitted to be smaller than the ungrounded conductors
where the maximum demand of a range of 8 3⁄4-kW
or more
rating has been calculated according to Column C
of Table 220.55, but such conductor shall have an ampacity
of not less than 70 percent of the branch-circuit rating and
shall not be smaller than 10 AWG.


PS. IIRC, that is Dennis Alwon's proposal.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
Oh Yeah correct i just read it too quickly.

I think the manufacturers could just use 240 clocks and control panels (like EU models) since they dont use a neutral for anything else.
Then ranges could go back to 3 wire and use a 6-50.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I have had to shake my head a few times at the cmp's decisions and responses. I will say I got a few accept and a few accepted in principle. Not bad, IMO for a first timer. I had written another one where their response was totally off- I posted it here a few months back.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
And have you seen the weird stuff that whack job Williams proposed?:p
A lot more than I proposed I know. You are busy at it. I really never thought that I would ever write a proposal but I also never thought I would be a mod either. Funny how things go.
 