proposal 2-134 said:Recommendation: Add new text to read as follows:
210.19(A)(5) Grounded Conductor. The size of the branch circuit grounded
conductor shall not be smaller than that required by 250.122, except that
250.122(F) shall not apply where grounded conductors are run in parallel.
Substantiation: As the code is now, it is possible, although a rare occurrence,
where one could reduce a branch circuits grounded conductor?s size smaller
than the ungrounded conductors and the equipment grounding conductor, but
under 210.19(A)(4) it is possible. In 215.2(A)(2) for feeders we have guidance
that the grounded conductor must not be smaller than the EGC that is required
in Table 250.122. We are not given that same assurance for a branch circuit. I
believe it is never the intent of the NEC to allow a grounded conductor to be
smaller than the required equipment grounding conductor.
Panel Meeting Action: Reject
Panel Statement: It is unclear to the panel how the submitter is interpreting
that 210.19(A)(4) could result in a grounded conductor smaller than the
ungrounded conductors and the equipment grounding conductor.
Number Eligible to Vote: 11
Ballot Results: Affirmative: 11
________________________________________________________________
Here was a interesting proposal dealing with L-N faults, any set of wires in a circuit should be capable of tripping the OCPD. If for some reason the ECG is increased in size beyond the size in 250.122 the neutral (read grounded conductor) can be smaller than the ECG but not smaller than 250.122. Seems fine with since conduit could be the EGG or the ECG could be upsized for sharing with a larger circuit. OK Looks like a good proposal.
Now I am not getting the reasoniong why the panel rejected it?
210.19(A)(4) permits conductors to be sized at an ampacity sufficient for the loads served.
Seems like neutrals need to be sized for the neutral load.
Where in the NEC are multi wire branch circuit conductors required to all be the same size for say a hot tub?
Did the panel not consider a standard 11kw hot tub with #6cu THHN, ECG of 8 THHN (oversized) and a 14 AWG neutral. It has a 750W neutral load for a light and blower, what is preventing someone from pulling a 14awg neutral?
Thanks
The proposal could have removed the 210.19 (3) exception #2 that requires a 10AWG neutral on a 2.5 kw 3 wire 20A counter top cooker circuit as well.