I know I'm digging up old bones and I have read several previous threads on the subject, but, I still find it difficult to answer the question when it comes up in the field.
I understand that conduit body dimensions must meet 314.28 when conductors are #4 or larger unless the conduit body is marked for fill. With that in mind, if a 1" LB is marked "Max Fill (3) #4 RHW" and we are installing (4) #4 THWNs in a 1" EMT can that 1" LB be used ?
314.28 references Table 1 Chapter 9. In that table my (3) RHW would have an area of .3999 where my (4) THWNs would be .3296
If that makes the THWNs allowable, would any combination of conductors with an area less than the (3) RHWs be allowable ?