EGC Outside the try cable feeder

Status
Not open for further replies.

jbolen

Senior Member
Looking at a project and there are several 6/3 feeders with #6 EGC on the outside of the try cable....???

Does this refer back to 300.2 or is it different for feeders.
 

jumper

Senior Member
Looking at a project and there are several 6/3 feeders with #6 EGC on the outside of the try cable....???

Does this refer back to 300.2 or is it different for feeders.

:? 300.3(B) maybe.

300.3 Conductors.

(B) Conductors of the Same Circuit. All conductors of
the same circuit and, where used, the grounded conductor
and all equipment grounding conductors and bonding conductors
shall be contained within the same raceway, auxiliary
gutter, cable tray, cablebus assembly, trench, cable, or
cord, unless otherwise permitted in accordance with
300.3(B)(1) through (B)(4).
 